About the ETAP Electrical Engineering Community Group
Have something to say?
Join LinkedIn for free to participate in the conversation. When you join, you can comment and post your own discussions.
Join LinkedIn-
Loading problem when paralleling generators
I have three generators connecting to a paralleling gear and they are in different distances. The problem is somehow ETAP does not...
Most Popular Discussions
MCCB coordination - etap
hi, when we are doing MCCB coordination in etap, it is asking for a parameter called TCC( it is the maximum clipping current). but on ...

ETAP cable editor problem
If I will input 4 sets 4c-70mm2 or any size as long as 4C cable. It always appear as 3sets in olive single line diagram. If I will input ...

Governor Modelling "Diesel Generator" UG8
I am modeling a Diesel generating set (EDG) with the UG8 Governing System. I have a problem with my absolute rotor angle results. My ...



A default current multiplier for 3-winding transformer inrush point that ETAP gives is based on the FLA of Sec. How many inrush currents...
Should I correct the multiplier to calculate the inrush current based on the FLA rating of Prim.?


Short circuit contribution by a fuse+contactor connected MV motor.
Dear Friends,
Can you please explain the short circuit current contribution by the motor in case of three phase fault on the bus. The ...

Dear all, I need your help in ETAP 6 (its for my Masters Degree)
I designed this electrical grid cause I'm studying harmonics analysis,
I added wind turbine generators which are already modelled in the ...